As long as the cable is not in contact with thermal insulation and is not bunched anywhere with any other cables then I cannot see a problem with the MCB being uprated to 50A (as long as it is definatley 10mm²)
 
OK so I was being on the cautious side - there was mention of cable installed in thermal insulation and of course none of us on here have seen the installation
 
Sponsored Links
Of course.

If the install is def. strictly Method 1, 10mm is OK.

If Method 4, 16mm.
 