Moving an upstairs Rad - no drain valves

Joined
14 Jul 2005
Messages
133
Reaction score
0
Location
Yorkshire
Country
United Kingdom
Hi,

I'm almost ready to move a bedroom Rad to the oposite wall, due to deco etc:- This is on a sealed system. Was hoping to get a few more pointers prior to doing the job, mainly on draining down the system. I know how to refill through the filling loop as i've removed a Rad before, but never done a drainoff.

This is the steps I'm going to take - please advise if this is not correct - Many-Thanks

(1) turn off Combi power
(2) Turn off Stopcock (clockwise)
(3) Fit a self cutting valve on downstairs kitchen rad (got no drain valves)
(4) shut both valves off on all upstairs Rads, apart from the one moving
(5) open all upstairs bleed valves to help with the drain flow.
(6) Finally drain the system via the newly fitted valve

That's about all i've got. After draining, will the Rad i'm moving still have water in it. It's a big rad and i may struggle to empty it on my own?

Thanks for any help
 
Sponsored Links
1 ok
2 no need to
3 ok
4 no need to
5 if you shut all the rad valves apart from one your working on, opening all the bleed valves won't gain anything with rad valves shut.
6 ok
 
Thanks for the info.

So from your response i don't need to shut off any of the rads when draining the system. I was told by closing the valves would speed up the drain process that's all.
 