I would say that it's pretty clear in terms of being "at least as good as" something which is deemed to be satisfactory. Even if the loads connected to the three proposed FCU's were a full 3A each, that would still be only 9A on the spur. Even with just a single 13A socket on a spur, the connected load could be 13A. With a double socket, it could be higher.
And with 3 spurs it could be 39A.
It seems that you and John believe that you would have exercised reasonable skill and care in preventing the load on that spur cable becoming 39A by sticking labels on the FCUs.
I do not, any more than I would accept it with sockets on the spur, or indeed with sockets on a ring so close together and/or so close to the origin that a notice warning people not to use them all at once and/or not to use them for significant loads for long periods was needed.
How about the warnings on 13A "strips" indicating that although there are four or five sockets the maximum connected load must not exceed 13 amps?
Utterly pointless. I've never understood why they have them, because the load is limited to 13A by the fuse in the plug.
What if the labels on the FCUs fall off or fade? Are there recognised standards for their durability which would give them acceptable permanence?
Are there any other areas in BS 7671 where something non-compliant can be made so by affixing a notice? (Note that's not the same as something always requiring one.)
Imagine reading a post here like this.
"I've just moved into a new house, and I've found a spur from a ring main with 3 fused switches on it. They're all supplied by the same cable, it's not a case of 2 of them running from the 3rd.
Is this OK?"
What percentage of replies do you think would advise either putting them on the ring or rewiring it so that 2 are on the load side of the 3rd, or adding a 4th with all of them on the load side of that, and what percentage do you think would advise putting labels on the FCUs to prevent an overload?
Quite honestly the more I think about your idea that labelling counts as reasonable skill and care the more it beggars belief.
If you were aiming for the best possible design, would you be using rings with spurs in the first place, bearing in mind all the limitations they bring with them?
I probably wouldn't, not as a default.
But rings are
explicitly allowed, and they do have characteristics which could make them a reasonable design.
For the life of me I cannot see why 3 FCUs with labels is reasonable when weighed against the alternative of 4 FCUs.
Is the maximum connected load less than the current rating deemed to be the maximum for the spur?
No more so than it would be with 3 labelled sockets.