Multiple feeds to grid switches

Discussion in 'Electrics UK' started by WeatherMan, 23 May 2010.

  1. WeatherMan

    WeatherMan

    Joined:
    28 Aug 2007
    Messages:
    6
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Is it permissable to have two feeds into a grid switch?

    I'd like to combine 6 ways (one 20A feed) with 2 ways (second 20A feed) in one 8 way grid box.

    I'm asking because I can see that you would need to trip two MCBs before opening the grid - ie no single point of supply.

    NB I'm NOT proposing any cross-connection between the "6 feeds" and the "2 feeds" so electrically it's OK - just a possible future safety issue if a switch replacement is needed.

    The total load for the combined 8 ways is over 20A - hence the need for 2 supplies.

    Thanks

    Mike
     
  2. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,403
    Thanks Received:
    1,823
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Yes it is. The MK grids have a warning label re multiple feeds and the need to completely isolate the grid.
    Good to pop warning notice on the CU too.
     
    • Thanks Thanks x 1
  3. ColJack

    ColJack

    Joined:
    16 Feb 2007
    Messages:
    11,793
    Thanks Received:
    409
    Location:
    West Midlands
    Country:
    United Kingdom
    what the hell are you lighting that requires 20A worth of lights?
     
  4. londonboy

    londonboy

    Joined:
    22 Feb 2009
    Messages:
    1,582
    Thanks Received:
    149
    Location:
    London
    Country:
    United Kingdom
    Who mentioned lighting? :)
     
  5. OwainDIYer

    OwainDIYer

    Joined:
    5 May 2010
    Messages:
    4,425
    Thanks Received:
    670
    Location:
    Stirlingshire
    Country:
    United Kingdom
    Yes, because most MCBs are only single pole devices so they do not count as isolators, which should switch all poles. Isolation for maintenance means using the Big Red Switch on most domestic installations, unless they're fairly recent and have everything on DP RCDs or RCBOs.

    A label inside the switch is a good idea though.
     
    • Thanks Thanks x 1
  6. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,021
    Thanks Received:
    280
    Country:
    United Kingdom
    MCBs do get used for maintenance isolation. Whether they should is a contentious point but they do and installers should keep that in mind when they install.
     
  7. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    18,403
    Thanks Received:
    1,823
    Location:
    Oxfordshire
    Country:
    United Kingdom
    Careful with your assumption. IIRC many (single module) RCBOs only switch the line - they have solid neutral connection.
     
    • Thanks Thanks x 1
  8. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    1,668
    Thanks Received:
    77
    Location:
    Kent
    Country:
    United Kingdom
    Good heavens I had never given this a thought.

    Many thanks.
     
  9. WeatherMan

    WeatherMan

    Joined:
    28 Aug 2007
    Messages:
    6
    Thanks Received:
    0
    Location:
    Yorkshire
    Country:
    United Kingdom
    Thanks to all

    A single 8 way grid and labels it is.

    (It's not lighting BTW)
     