Myson Apollo HW but no Heating

Joined
4 Apr 2007
Messages
42
Reaction score
0
Country
United Kingdom
All of a sudden my heating does not work.

HW is fine boiler fires no problem, but CH does not fire.

Any ideas?

Cheers
 
Sponsored Links
Have you 2 x 2port zone valves or 1 x 3 port valve. If so I would suspect 3 port head or ch 2 port valve head.

Checked room stat?
 
Checked room stat and all ok,

Just found the mid position valve (assume thats what you mean by a 1 x 3 port valve) in the airing cupboard and it seems to be stuck on the W, there is a plstic type switch but it won't seem to budge.
 
If you can, remove head and see if spindle is stuck. If not replace head. If it is stuck then new complete unit needed ;)
 
Sponsored Links
Cheers, i'll have a look in the morning.

I can no move it manually to the "M" position, but it just slowly drifts back to W, what would happen if I wedged it in the M piositio for a while?
 
heating & h/w should get hot but with no thermostatic control. If you do this and rads get hot then this proves valve faulty ;)
 
Cheers,

Yer held it open for a few minutes and the rads warmed up, so it must be that then - couldn't be anything else though could it??
 
Could just check that stat controling it is sending 240V to it first ;)
 