Hi Folks,
My parents have a heating system as follows: (Fitted by British Gas).
Ideal Mexico Super 2 RS50
Horstmann Tiara H425 controller
Room stat
Fully pumped system
3 way mid position valve
Their issues appear to be 2 fold.
1. Ever since this system was fitted the DHW was only available when the CH was on or in other words the CH & DHW are NOT independant.
I understand there are 2 ways of wiring the Tiara H425 controller i.e. For a pumped system or a gravity system - would i be right in thinking that this may have been wired for a gravity system which i understand would result in the 'non independant' operation of the controller?
If the DHW is seleted on 'constant' nothing happens - only when the CH is activated does the DHW appear to kick in. They normally set the room stat to zero so that the radiators don't actually heat up.
In addition... they haven't used the heating all summer (we had a summer?) and the first time they used it (recently) they turned the room stat up quite high - now when they put the CH on to activate the DHW they can't stop the rads heating up - even by setting the room stat to Zero.
I'm only an IT dude with limited plumbing/heating experience and can see that there are many 'possible' areas of failure e.g. the controller/room stat/cylinder stat/mid position valve. I was wondering if anyone may be so bold as to suggest a 'Probable' point of failure ??
After confirming that the controller is wired up correctly (i now have the diagram) i think i may try (in the following order)
1. bypassing the controller to see if the DHW fires up the boiler - if yes the controller is faulty?
2. If the DHW still doesn't fire up - bypass the cylinder stat?
3. unsure about the Mid position valve as i've already been manually adjusting with no effect.
Any pointers gratefully accepted !
Ian
My parents have a heating system as follows: (Fitted by British Gas).
Ideal Mexico Super 2 RS50
Horstmann Tiara H425 controller
Room stat
Fully pumped system
3 way mid position valve
Their issues appear to be 2 fold.
1. Ever since this system was fitted the DHW was only available when the CH was on or in other words the CH & DHW are NOT independant.
I understand there are 2 ways of wiring the Tiara H425 controller i.e. For a pumped system or a gravity system - would i be right in thinking that this may have been wired for a gravity system which i understand would result in the 'non independant' operation of the controller?
If the DHW is seleted on 'constant' nothing happens - only when the CH is activated does the DHW appear to kick in. They normally set the room stat to zero so that the radiators don't actually heat up.
In addition... they haven't used the heating all summer (we had a summer?) and the first time they used it (recently) they turned the room stat up quite high - now when they put the CH on to activate the DHW they can't stop the rads heating up - even by setting the room stat to Zero.
I'm only an IT dude with limited plumbing/heating experience and can see that there are many 'possible' areas of failure e.g. the controller/room stat/cylinder stat/mid position valve. I was wondering if anyone may be so bold as to suggest a 'Probable' point of failure ??
After confirming that the controller is wired up correctly (i now have the diagram) i think i may try (in the following order)
1. bypassing the controller to see if the DHW fires up the boiler - if yes the controller is faulty?
2. If the DHW still doesn't fire up - bypass the cylinder stat?
3. unsure about the Mid position valve as i've already been manually adjusting with no effect.
Any pointers gratefully accepted !
Ian