8mbar, normally we would expect to see a minimum of 18mbar. Why didn't the Alpha eng. leave warning notice paperwork and explain the situation?
You may need to find another gas installer to sort this out...he's clearly an idiot.
If he kicks off give Gas-Safe a ring an request an inspection...tell them you've no hot water.
What was the previous boiler make and model...it's possible it was smaller Kw rating and the burner ignited at very low gas pressures.
I can only think the boiler is actually igniting with a hot water demand but as the burner ramps up to maximum the burner then extinguishes due to the low incoming pressure although many modern boilers can cope.
You may need to find another gas installer to sort this out...he's clearly an idiot.
If he kicks off give Gas-Safe a ring an request an inspection...tell them you've no hot water.
What was the previous boiler make and model...it's possible it was smaller Kw rating and the burner ignited at very low gas pressures.
I can only think the boiler is actually igniting with a hot water demand but as the burner ramps up to maximum the burner then extinguishes due to the low incoming pressure although many modern boilers can cope.