Hello apologies in advance for my absolute lack of electrical/ central heating/ plumbing knowledge, but really hoping someone on here can kindly assist me
I currently have no HW or CH. There is currently no signal coming out of the 3 port valve to tell the boiler to fire up. I have tried a replacement 3PV and still no signal from the orange wire so I don’t think the 3PV is the issue. Inputs from the room thermostat are 230v when on and 0v when off so I don’t think this is the problem.
When CH and HW or only HW is selected from the programmer the 3PV motors to the correct position. Between the programmer and 3PV I get
230v with both CH and HW turned off
70v with both CH and HW turned on
0v with only HW turned on
Do these changes in voltage sound correct? Or does this indicate a fault with the programmer?
Any help massively appreciated, I’m not too sure what else to try.
I currently have no HW or CH. There is currently no signal coming out of the 3 port valve to tell the boiler to fire up. I have tried a replacement 3PV and still no signal from the orange wire so I don’t think the 3PV is the issue. Inputs from the room thermostat are 230v when on and 0v when off so I don’t think this is the problem.