Hi All, new to commenting on this forum but have always been impressed with the quality of advice so here goes. Have been called out to a boiler always on among other faults. Replaced 3PV, which was faulty, and completed other task. However, boiler still on, receiving power from 3PV even though room and cyl stats turned off and programmer set to off.
The customer had lots of work done in the past so I rewired wiring centre and had the same problem. The LR connection at the boiler was receiving power and I traced it to the 3PV. It was sending a 70v signal to the boiler when dormant. It did send the correct 240v when meant to but the 70v is enough to keep it going.
I swapped out the 3PV and still had same problem. Are there any 3PV's which have a 0v when idle? Any other ideas? Customer has to turn off dial at boiler when not required. I've asked around and no-one can shed any light on it or suggest anything that I haven't tried. Look forward to the responses. Thanks.
The customer had lots of work done in the past so I rewired wiring centre and had the same problem. The LR connection at the boiler was receiving power and I traced it to the 3PV. It was sending a 70v signal to the boiler when dormant. It did send the correct 240v when meant to but the 70v is enough to keep it going.
I swapped out the 3PV and still had same problem. Are there any 3PV's which have a 0v when idle? Any other ideas? Customer has to turn off dial at boiler when not required. I've asked around and no-one can shed any light on it or suggest anything that I haven't tried. Look forward to the responses. Thanks.