Hi All,
Looking for some help. Pic attached shows two 22mm rad pipes coming out of the hallway (concrete floor) into suspended timber floor and are messing with my plans to run a joist along the wall where they come out. The joists are 100mm which means I can notch max 12.5mm from them. However the top of the joist needs to sit at least just above the top of the pipe - that would require say a 25mm notch, double the Eurocode recommendations.
So how can I get that joist in close to the wall? Notching seems out of the question, any thoughts really appreciated.
Thanks
Looking for some help. Pic attached shows two 22mm rad pipes coming out of the hallway (concrete floor) into suspended timber floor and are messing with my plans to run a joist along the wall where they come out. The joists are 100mm which means I can notch max 12.5mm from them. However the top of the joist needs to sit at least just above the top of the pipe - that would require say a 25mm notch, double the Eurocode recommendations.