I have only recently read that the No Trip Zs function of my meter shouldn't be relied upon. Instead the calculated value should be used in my test results. I have always gone with the understanding that the result can be "calculated or measured"
Current job has thrown up some interesting results.
Ze=0.13
1. 32A Type B Ring Final circuit. r1=0.34, rn=0.33, r2=0.59 Measured Zs is 0.36 yet calculated would be 1.06
2. 32A Type B Ring Final circuit. r1=0.55, rn=0.55, r2=0.94 Measured Zs is 0.50 yet calculated would be 1.62
As you can see circuit 1 would satisfy disconnection time (max for 32A type B = 1.16) with either calculated or measured. Circuit 2 however would be ok for measured but not calculated.
Parallel paths obviously play some part in the difference between the calculated and measured results but I didn't think the difference would be so great.
So I guess the question/advice required here is should I rely on the measured Zs value or not? If not then I need to look at circuit 2.
Current job has thrown up some interesting results.
Ze=0.13
1. 32A Type B Ring Final circuit. r1=0.34, rn=0.33, r2=0.59 Measured Zs is 0.36 yet calculated would be 1.06
2. 32A Type B Ring Final circuit. r1=0.55, rn=0.55, r2=0.94 Measured Zs is 0.50 yet calculated would be 1.62
As you can see circuit 1 would satisfy disconnection time (max for 32A type B = 1.16) with either calculated or measured. Circuit 2 however would be ok for measured but not calculated.
Parallel paths obviously play some part in the difference between the calculated and measured results but I didn't think the difference would be so great.
So I guess the question/advice required here is should I rely on the measured Zs value or not? If not then I need to look at circuit 2.