From what I understand, a non-bidirectional RCD/RCBO isn’t automatically a C2 just on its own. It really depends on whether it still provides effective protection for the circuit it’s feeding and whether it’s installed in line with the manufacturer’s instructions. .... A lot of these devices are only designed for supply from one direction, so if they’re wired the “wrong” way round they may not operate correctly under fault conditions.
Unless you know something that the rest of us don't, it would seem that a traditional RCD will, 'initially', provide the required fault protevtion (for currents travelling either way through it).
As being discussed in this and other current threads, the potential problem arises if someone subsequently presses the test button whilst current is flowing 'backwards' (from a generator or inverter) through a traditional ('unidirectional') RCD and keeps the button depressed for a while after the device trips. Per the video that eric has referenced, that may result in destruction of the electronics of the RCD, resulting in a situation in which it would no longer provide fault protection (with current flowing in either direction).
.... It really depends on ..... whether it’s installed in line with the manufacturer’s instructions. .... A lot of these devices are only designed for supply from one direction, so if they’re wired the “wrong” way round they may not operate correctly under fault conditions.
As we have discussed, many (perhaps most?) traditional ('unidirectional') RCDs do not bear any indication of which way around they should be installed, and nor does associated documentation give any instructions/guidance about this.
That’s where an electrician would normally flag it during an EICR — but whether it’s C2 or just C3 tends to come down to actual risk and compliance, not just the wording on the device.
The potential/theoretical risk (related to use of the test button) will surely be identical in all situations, so there will be no rational/logical basis on which an electrician could 'choose' between C2 and C3 in relation to a particular installation, will there?
In practice, I’ve seen it recorded both ways depending on the tester’s interpretation, so there isn’t always a strict blanket answer.
Quite - it's just down to the view of the tester (which, as above, should really be 'consistent' for all EICRs they do) - which is a pretty unsatisfactory situation.
One thing that hasn't been discussed much is that 'plug in solar' systems are 'portable' and hence, by definition, could be plugged in, at any time, into any socket in any house/installation. That really means that if an inspector believed that an inverter plugged into a socket protected by a unidirectional RCD deserved a C2, and also believed (which I personally don't) that the scope of an EICR should consider what was (
or could be) plugged into any of the sockets, then that inspector would logically give a C2 to every unidirectional RCD protecting a sockets circuit in every installation they inspect, even if there is currently no evidence that the household possesses a 'plug in solar' system ??