Just been to look at checking out some wiring in a friends house he has bought, basically give it the once over..
Wiring is in a right state..
Three consumer units, no fuse carriers present, bedroom in garage, with 2x 6.0mm t&e over head, one for a shower, one for a garage CU.
Outside lights wired via extension leads..
No Earth Terminal provided by REC, except a 2.5mm earth cable coming from bottom of cut out. (didnt have earth loop tester with me at the time)
2.5mm earth cable goes to lower cu, Old wylex (didnt check to see what this powered.. wasnt interested - Earth loop of sockets was 5.17 iirc.
Top Consumer unit had earth bonding cable (10mm) from gas iirc Havent confirmed yet connected in.. this got a reading of 5.17 on the earth connection in cu)
Shower CU mounted upside down above top cu (no - poor earth) was fed from CU via 30A Rewireable fuse.. only rcd fitted, centrally with 1/2 blank either side.
So 30a Fuse - 63A RCCD - overhead cable - Shower in garage with no earth..
Took one look at the above.. looked at main fuse there was enough tag / seal to remove it and leave it intact.. Nice
Removed both boards and one set of tails from henly.. (one set corroded / loose / burnt)
Reinstalled shower cu correct way up, put tails into RCD 2.5mm out from Neutral, and installed a spare 16A breaker of odd make next to it.. bridged RCD to breaker with 10mm cable as no bus bar, and connected live to breaker.
took 2.5mm from cut out.. and connected this to a double socket mounted below the temporary CU (which will be now be mine mounted on a portable board)
Removed everything else.. Earth Loop Impediance now 0.17
Got someone going in to rip out all exisiting cabling / wiring / patresses.. at least its reasonably safe. Have asked homeowner to ask YE / NEDL to come and install an earth terminal ASAP.
I will get some pics of the appauling wiring remaining, and of my install when done.. just for your amusement.
Had to share this rant.. (I had to sort this there and then it was that bad.)
David
Wiring is in a right state..
Three consumer units, no fuse carriers present, bedroom in garage, with 2x 6.0mm t&e over head, one for a shower, one for a garage CU.
Outside lights wired via extension leads..
No Earth Terminal provided by REC, except a 2.5mm earth cable coming from bottom of cut out. (didnt have earth loop tester with me at the time)
2.5mm earth cable goes to lower cu, Old wylex (didnt check to see what this powered.. wasnt interested - Earth loop of sockets was 5.17 iirc.
Top Consumer unit had earth bonding cable (10mm) from gas iirc Havent confirmed yet connected in.. this got a reading of 5.17 on the earth connection in cu)
Shower CU mounted upside down above top cu (no - poor earth) was fed from CU via 30A Rewireable fuse.. only rcd fitted, centrally with 1/2 blank either side.
So 30a Fuse - 63A RCCD - overhead cable - Shower in garage with no earth..
Took one look at the above.. looked at main fuse there was enough tag / seal to remove it and leave it intact.. Nice
Removed both boards and one set of tails from henly.. (one set corroded / loose / burnt)
Reinstalled shower cu correct way up, put tails into RCD 2.5mm out from Neutral, and installed a spare 16A breaker of odd make next to it.. bridged RCD to breaker with 10mm cable as no bus bar, and connected live to breaker.
took 2.5mm from cut out.. and connected this to a double socket mounted below the temporary CU (which will be now be mine mounted on a portable board)
Removed everything else.. Earth Loop Impediance now 0.17
Got someone going in to rip out all exisiting cabling / wiring / patresses.. at least its reasonably safe. Have asked homeowner to ask YE / NEDL to come and install an earth terminal ASAP.
I will get some pics of the appauling wiring remaining, and of my install when done.. just for your amusement.
Had to share this rant.. (I had to sort this there and then it was that bad.)
David