one pipe system

Joined
15 Sep 2005
Messages
89
Reaction score
55
Location
Hampshire
Country
United Kingdom
Got called out to repair a leak in a solid floor, and noticed it was a one pipe system 22mm, the section of pipe i cut out had two 15mm centre tees that supplied the lounge rad and inbetween the tees the section of pipework about 100mm apart had some kind of internal reducer, and then carried on with the circuit.The radiator has a trv at low level, and also a lock shield valve at low level at the other end. On refilling all radiators and repaired pipework gets very hot apart from this teed off rad. I did not replace the reducer and was wondering if this would be the problem. Would a non return valve help, the radiator worked fine before. Any suggestions would be appreciated.
 
Sponsored Links
Sounds like a bypass with a restriction to encourage flow through the rad, you've removed the restriction so the water takes the easiest route, bypassing the rad. You'll either need to reinstate it, put a proper auto bypass in, or cap off the bypass so all the water flows through the rad, change the TRV for a lockshield and install a roomstat linked to the boiler.
 
Sponsored Links
It's similar to an injector tee, in that it creates a venturi effect (low pressure zone) which encourages circulation through the radiator. :rolleyes:
 