Thats a pretty powerful pump and will circulate say 0.8m3/hr, 13.3LPM , at a head of 5.8M on speed3, which quite likely will cause pump over on even a clean OV system especially in a bungalow, suggest changing to speed1, this pump will still circulate 0.8m3/hr at a 3.0M head which should satisfy your requirements. On this speed, once you have vented all the air, see if you are getting pump over through the vent, also, get someone to start/stop the pump and watch for any pump over while the pump is starting or/and stopping, if not, and the rads are a bit slow in heating try speed2, 0.8LPM at 4.3M and repeat the tests.