S
scotteng
hi, just been to a customer who had a periodic inspection carried out and wants me to fix the faults found on it. The property is a ground floor 2 bed flat, meter is in the flat, main fuse is about 100 yards away at the other end of the building.
ok, the main earthing looks to be only 6mm, and is not pvc sheathed, just the old fabric type. The ze tests shows 0.16, which is well within for TNS system. But 6mm is well below regulations, would this need upgrading to make the installation 'satisfactory'? what recommendantion code should this be?
the meter tails are only 16mm, single pvc sheather, again not up to current regs.
No code has been put on the report or any recommendations to upgrade.....
your thoughts would be helpfull!
plus if the earth was to be upgraded, and ideas of how to go about it, as it runs through the cavity wall of about 4 other flats before it gets to the switchboard to the block of flats!!
cheers guys
ok, the main earthing looks to be only 6mm, and is not pvc sheathed, just the old fabric type. The ze tests shows 0.16, which is well within for TNS system. But 6mm is well below regulations, would this need upgrading to make the installation 'satisfactory'? what recommendantion code should this be?
the meter tails are only 16mm, single pvc sheather, again not up to current regs.
No code has been put on the report or any recommendations to upgrade.....
your thoughts would be helpfull!
plus if the earth was to be upgraded, and ideas of how to go about it, as it runs through the cavity wall of about 4 other flats before it gets to the switchboard to the block of flats!!
cheers guys