what code would you put on finding low voltage (12volt) in a consumer unit?, looks like alarm cable being used to operate contactors for E7 heating
Or a 4
Prevention of detrimental mutual influence. Mixing Band 1 and 2 circuits.
"Extra Low Voltage circuits should not be run in the same wiring system as 230v circuits unless all ELV cables and conductors are insulated for 230v or separated by an earthed metal screen. Reg:528.1"
.
"Extra Low Voltage circuits should not be run in the same wiring system as 230v circuits unless all ELV cables and conductors are insulated for 230v or separated by an earthed metal screen. Reg:528.1"
"Extra Low Voltage circuits should not be run in the same wiring system as 230v circuits unless all ELV cables and conductors are insulated for 230v or separated by an earthed metal screen. Reg:528.1"
Three questions about ELV cables in a 230 volt consumer unit.
Does insulated for 230v allow for a over heating component or conductor ( loose terminal in an MCB for example ) melting the insulation ?
If it does not then an earthed metal screen would appear to be needed.
How would one fit that screen into a consumer unit ?
Would the screen in a screened ELV cable be considered acceptable even though its current carrying ability ( in fault conditions ) is seldom specified ?
My opinion is that ELV circuits and SELV circuits should never enter the high risk area of a consumer unit.
It makes it easier for Bernard to unseparate the separated ELV output by connecting it to earth, as there'll be an earth bar handy.