Someone familiar with PHE calculations (SimonH2??) might have a look at this and comment/correct.
Someone asked me to have a look at the output from a Nordic BA 23-40 165kw PHE, all their PHEs have a heat transfer coefficient of 6200W/M2 deg C. the known inputs are primary flow 33.76LPM at 53C, required secondary temperature 48C from cold water at 5C, my calculations below show that the 0.92M2 Hx should give a output of 63.59kw with a secondary flowrate of 21.2LPM. Nordic technical inform me that a 1.98M2 Hx is required (closest Hx is their 2.24M2) to give these outputs/flowrates, am awaiting a reply as to why this is.
Someone asked me to have a look at the output from a Nordic BA 23-40 165kw PHE, all their PHEs have a heat transfer coefficient of 6200W/M2 deg C. the known inputs are primary flow 33.76LPM at 53C, required secondary temperature 48C from cold water at 5C, my calculations below show that the 0.92M2 Hx should give a output of 63.59kw with a secondary flowrate of 21.2LPM. Nordic technical inform me that a 1.98M2 Hx is required (closest Hx is their 2.24M2) to give these outputs/flowrates, am awaiting a reply as to why this is.