Hi all
I have a Potterton Performa on which we turned on c/h about a week ago. Last couple of days the shower started cooling/warming subtley and yesterday quite definate cycle. Today the ch and dhw stopped completely.
If I reduce flow in c/h circuit by half closing one of the valves on the magnoclean filter I can get the boiler to cycle on for 18 seconds every three minutes to keep the radiators warmish (have an infant that needs being kept warm). Can't get any dhw though.
Have had the plate heat exhanger off this evening and cleaned as much as I could by flushing whilst tapping with a hammer - visibly improved flow.
However, still same.
What likely? Primary Heat exchanger?
Have tried to get someone to look at it over the weekend but no joy so looks like on my own. (unless anyone can recommned someone in St Albans who'll do weekend work?
regards