Recently my Potterton statesman Flowsure+ started to trip out on the limit thermostat - generally during the night without the CH calling for heat - and therefore required manual reset in the morning.
Couldn't fault the system as never actually saw a overheat on the temp gauge and I would have liked more time for fault finding but the 'tribes ' were turning up for xmas dinner! Due to the time of year and possible unavailability of parts over this period I have replaced both the Limit Stat and the Boiler Stat.
Things ok for 2 days then same problem. This time witnessed overheat. Reset Limit Stat - fine. Then next day no CH - system calling for heat with boiler temp of approx 65 degrees. Overheat lamp not illuminated. Pump (CP53) and all pipes close to boiler were hot - but obviously no flow. Carried out pump bleed and rad bleed -system ok. Noticed arcing noise coming from pump control box, stripped it down and found poor contact between selector switch rotary and stationary contacts. One cause for open circuit giving no flow.
I have since had the same problem a number of times but have found the pump switch to be made( Speed III) and the only way to get the pump running is to perform a manual start ie by unscrewing the nut at the end of the motor shaft.
1) I know the selector switch issue is a problem - can I buy just the control housing?
2) The system is fitted with a pump overrun stat and from the wiring diagram the pump should be running all the time - I am going to wire the pump from a 3-pin plug to eliminate the stat. Good or bad idea? Could it be a cause?
3) Could there be an airlock stopping pump? If so how do I get rid?
4) Am I barking up the wrong tree?
Thankyou for your assistance.
Couldn't fault the system as never actually saw a overheat on the temp gauge and I would have liked more time for fault finding but the 'tribes ' were turning up for xmas dinner! Due to the time of year and possible unavailability of parts over this period I have replaced both the Limit Stat and the Boiler Stat.
Things ok for 2 days then same problem. This time witnessed overheat. Reset Limit Stat - fine. Then next day no CH - system calling for heat with boiler temp of approx 65 degrees. Overheat lamp not illuminated. Pump (CP53) and all pipes close to boiler were hot - but obviously no flow. Carried out pump bleed and rad bleed -system ok. Noticed arcing noise coming from pump control box, stripped it down and found poor contact between selector switch rotary and stationary contacts. One cause for open circuit giving no flow.
I have since had the same problem a number of times but have found the pump switch to be made( Speed III) and the only way to get the pump running is to perform a manual start ie by unscrewing the nut at the end of the motor shaft.
1) I know the selector switch issue is a problem - can I buy just the control housing?
2) The system is fitted with a pump overrun stat and from the wiring diagram the pump should be running all the time - I am going to wire the pump from a 3-pin plug to eliminate the stat. Good or bad idea? Could it be a cause?
3) Could there be an airlock stopping pump? If so how do I get rid?
4) Am I barking up the wrong tree?
Thankyou for your assistance.