pressure

Joined
17 Nov 2009
Messages
6
Reaction score
0
Location
Essex
Country
United Kingdom
hi i have a basi combo boiler i have just flushed the system,i put half a bar water pressure in the system because it should have one bar but for some un known reason it then goes up to 3 bar why is this and is it dangrous
 
Sponsored Links
no it rises overnight to 3 bar and stays there what should i do thanks
 
Boiler pressure rises only when heating is on = Expansion vessel as above

Boiler pressure rises even with heating turned off =
Likely- Filling loop is passing(remove filling hose to check)
Possibly- Plate heat exchanger is holed(isolate water to boiler over timed period to check)
 
Sponsored Links
thanks i ill check hope its not expensive i just took out the hot water heat exchanger and cleaned it i thought i was all done lol
 