Im off work so plenty of time to get myself tied up in knots over (Basic ) electrical theory, so....
I've been thinking about overload, in particular.
433.1.1 and appendix 4
My problem is where overload protection is not required.
And the use of design current, instead of the rated current of the protective device, when applying correction factors. Ci, Cf.....
Im talking domestic, light commercial here. I imagine there is all sorts of systems in place for industrial installations where loss of power could cause serious issue.
So
How is it even possible to omit overload protection?
I presume they are saying a correctly sized cable can handle the design current, and since the load can not be increased, overload protection is not needed , but fault protection is.
But since MCB's provide both its a bit of a mute point.
I read about 2.5mm2 TandE being on a 32A 60898 as an example of not factoring overload, but I would have thought that Ib≤In≤Iz prevents that
Is there such a thing as a fixed load, which can not cause an overload?
Thats not really the case is it? Could a shower /immersion or any fixed load, develop a fault which could cause an overload. If the resistance of the element decreased, the current would increase?
Also..
Equations.. 1-5
The book makes it appear that we only use In when we have a correction factor for the BS 3036 and for grouping. (equations 1 and 2)
But we can also use Cg in equation 5 (Ib)
Is it the case that we only use Ib when we don't have a BS3036 -
It makes it sound like overload protection is only needed when we have a BS3036.
But..
Playing around with cable calculations using Ib and In
Ib often suggests a lower CSA cable, which is only found to be unsuitable when doing the volt drop calculation
Ib often produced a Iz which is right on the edge of acceptability.
In gives you a bit of extra capacity. So is it not best to always use In
When would you use Ib?
Thanks...
I've been thinking about overload, in particular.
433.1.1 and appendix 4
My problem is where overload protection is not required.
And the use of design current, instead of the rated current of the protective device, when applying correction factors. Ci, Cf.....
Im talking domestic, light commercial here. I imagine there is all sorts of systems in place for industrial installations where loss of power could cause serious issue.
So
How is it even possible to omit overload protection?
I presume they are saying a correctly sized cable can handle the design current, and since the load can not be increased, overload protection is not needed , but fault protection is.
But since MCB's provide both its a bit of a mute point.
I read about 2.5mm2 TandE being on a 32A 60898 as an example of not factoring overload, but I would have thought that Ib≤In≤Iz prevents that
Is there such a thing as a fixed load, which can not cause an overload?
Thats not really the case is it? Could a shower /immersion or any fixed load, develop a fault which could cause an overload. If the resistance of the element decreased, the current would increase?
Also..
Equations.. 1-5
The book makes it appear that we only use In when we have a correction factor for the BS 3036 and for grouping. (equations 1 and 2)
But we can also use Cg in equation 5 (Ib)
Is it the case that we only use Ib when we don't have a BS3036 -
It makes it sound like overload protection is only needed when we have a BS3036.
But..
Playing around with cable calculations using Ib and In
Ib often suggests a lower CSA cable, which is only found to be unsuitable when doing the volt drop calculation
Ib often produced a Iz which is right on the edge of acceptability.
In gives you a bit of extra capacity. So is it not best to always use In
When would you use Ib?
Thanks...