puma problems

Joined
20 Oct 2009
Messages
30
Reaction score
1
Location
Lancashire
Country
United Kingdom
hi i've got a potterton puma 80E which isnt very well. When the central heating has been on for a few hours then turns off, when i come to use hot water in the morning there is no hot water and the low system pressure led is lit. I have to use the fill loop to refil the sytem. This happens every morning :( any ideas would help thanks .
 
Sponsored Links
hi i had a go a t represurising the pv with a foot pump didnt seem to build up pressure could the diaphram have failed? if i have another go and try for longer could i cause any damage if air is passing into the water side of the vessel?
 
Sponsored Links
Follow the FAQ on this site and repressurise it exactly as stated.

There are a number of possibilities. A blocked communication pipe is one of them!

Tony
 
thanks for the advise i followed the info on the faq and repressurised the expansion vessel and so far so good , had a happy central heating system for a week now thanks ur advise has saved me some of the green stuff and is much apreciated :)
 
Thanks for letting us know the advice worked for you.

Tony
 