Pump wrong way around

Joined
5 Dec 2020
Messages
13
Reaction score
0
Country
United Kingdom
Hi all,

Inherited this system.

When I turn the heating on, I was expecting heat to leave the boiler, through the pump and then hit the two zone valves, then go on its merry way.

Instead, it seekm the “return” pipe gets hot first and the “flow” is last to get hot.

Looking at the pump, it’s clear someone has replaced the head but left the old red body in place. Looking at the pump instructions, and pictures on Google, it seems the pump is pumping water through the filter, into the boiler and back out, so in reverse.
Do you agree with this and should I turn it around? There’s no issues with the system that I can tell having been here for 3 weeks. It all works fine.
IMG_2828.jpeg
IMG_2828.jpeg
IMG_2830.jpeg
IMG_2831.jpeg
IMG_2829.jpeg
 
Looks like it may be like that deliberately, the zone valves seem to be pointing towards the pump. Can you confirm which way the arrow is point on the zone valve body?

It was common to have the pump on the return on older systems.
 
Instead, it seekm the “return” pipe gets hot first and the “flow” is last to get hot.

I would double-check, if you have not done already, with the boiler manual - which is the flow and return at the boiler, so you are certain it's working backwards...

Looking at the pump, it’s clear someone has replaced the head but left the old red body in place.

What makes you think the pump head has been replaced?

The pump body, the red painted part, sets the direction of flow - so if the head has been replaced, it was pumping the wrong way from original install, or perhaps a the boiler has been replaced, where the pipe layout was different.

Either way, get it checked/corrected.
 
Thanks all,

I downloaded the manual.


9.2 The flow and return sockets are located at the rear of the

appliance, two at high level (flow) and two at low level (return).

Connection of the flow and return sockets can either be made on

diagonally opposite sockets or on the same side of the boiler.”

I followed the pipe from the pump into the boiler and it does indeed go into the return at the bottom ( it drops down behind the boiler despite looking like it goes into the top.

Seems it’s all fine.
 
Thanks all,

I downloaded the manual.


9.2 The flow and return sockets are located at the rear of the

appliance, two at high level (flow) and two at low level (return).

Connection of the flow and return sockets can either be made on

diagonally opposite sockets or on the same side of the boiler.”

I followed the pipe from the pump into the boiler and it does indeed go into the return at the bottom ( it drops down behind the boiler despite looking like it goes into the top.

Seems it’s all fine.

You could also run that UPS3 on either CC1, one sold green LED at 4.2M which will be sufficient for most systems, or, certainly, CC2, one solid green followed by one solid yellow LED at 5.2M which will satisfy 99% of systems, should have no need to run at CC3, one solid green followed by two solid yellows at 6.4M, rarely if ever required, Just press the setting button briefly to change settings.
 
Last edited:

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top