Just wanted to check my understanding.
Am I right that running single phase cabling (single core, sheathed) in conduit embedded in a wall (recessed ~ 40mm) falls under reference method A ? Which from table 4D1A would then make the maximum allowable current for 1.5mm sq. cable 14.5A ?
I've got some 1.5 mm sq. radial lines running from my CU that feed electric heating in my flat and I wanted to check that I've got the right MCB installed
For the purposes of calculations, is the harmonised 230V used or 240V ?