As to de-loader valves, yes there is some method used, three phase normally linked to star/delta starter, but single phase often simple time, converting a reciprocating compressor to inverter drive was not simple, as to vain compressors not so sure.
What matters is cooling, so 2 x 2.5 mm² does not equal 1 x 5 mm² as it is the surface area around the cable that matters. Permissible to use 1.5 mm² mineral cable for a ring final, but not ali-tube as the ali-tube cables does not transmit the heat to the outer casing as well as mineral cable.
As to EICR inspectors, when the MOT was introduced we had a book telling us what was and was not permitted, there was a little leeway, but all singing from same song sheet.
But 230 volt is potentially dangerous, what a silly phrase, so to have a type AC RCD on a circuit where you could get DC could be seen as potentially dangerous. Not seen as yet anyone award a code C2 for wrong type of RCD, but if they did then hard to say wrong, however the electrical safety council seems to think like many, if it complied in 1950 and nothing has changed then it still complies.
OK very unlikely nothing has changed, but it means if an electrician recommends improvement i.e. he has not totally missed faults while doing his drive by, i.e. a list of code C3's, then again hard to say he is wrong.
The EICR is designed to tell the owner the condition of the installation, i.e. cables which have insulation crumbling etc. It was never designed as a home MOT. However the person commissioning the inspection is free to say to what extent they want the inspector to go, so the LABC may tell an inspector to do it as close to an electrical installation certificate as he can, showing all non compliances. Or a prospective buyer may decide the home buyer report is good enough.
Love to know more about Pembrokeshire County Council Trading Standards v Mark Cummins trading as M C Electrics as this case seems to be far reaching, as it was vendor of a Milford Haven property who commissioned the inspection, but the current owner Nia Evans who got local electrician John Morley who in turn said the electrics were unsatisfactory which advised contacting STROMA, but it was Matthew Williams, a Council electrician, who carried out an inspection of the electrics at the property for Pembrokeshire County Council Trading Standards. But the report fails to say what was found, and why a report for the vendor was taken up by Pembrokeshire County Council Trading Standards. I could see the conveyancing solicitors raising a court case, but not Pembrokeshire County Council Trading Standards?
This house I had an EIC which was passed off as being for whole house, but was for the flat under the house, and I see no reason why I should be able to claim from the electricians working on the flat for errors in the main house, had it been an EICR for flat same would have applied.
Assuming that you are talking of 2.5mm² cable, as you imply, a ring with one socket together with an unfused spur wired with what is effectively 5mm² cable supplying three (or 30) further sockets is perfectly compliant.
What matters is cooling, so 2 x 2.5 mm² does not equal 1 x 5 mm² as it is the surface area around the cable that matters. Permissible to use 1.5 mm² mineral cable for a ring final, but not ali-tube as the ali-tube cables does not transmit the heat to the outer casing as well as mineral cable.
As to EICR inspectors, when the MOT was introduced we had a book telling us what was and was not permitted, there was a little leeway, but all singing from same song sheet.
But 230 volt is potentially dangerous, what a silly phrase, so to have a type AC RCD on a circuit where you could get DC could be seen as potentially dangerous. Not seen as yet anyone award a code C2 for wrong type of RCD, but if they did then hard to say wrong, however the electrical safety council seems to think like many, if it complied in 1950 and nothing has changed then it still complies.
OK very unlikely nothing has changed, but it means if an electrician recommends improvement i.e. he has not totally missed faults while doing his drive by, i.e. a list of code C3's, then again hard to say he is wrong.
The EICR is designed to tell the owner the condition of the installation, i.e. cables which have insulation crumbling etc. It was never designed as a home MOT. However the person commissioning the inspection is free to say to what extent they want the inspector to go, so the LABC may tell an inspector to do it as close to an electrical installation certificate as he can, showing all non compliances. Or a prospective buyer may decide the home buyer report is good enough.
Love to know more about Pembrokeshire County Council Trading Standards v Mark Cummins trading as M C Electrics as this case seems to be far reaching, as it was vendor of a Milford Haven property who commissioned the inspection, but the current owner Nia Evans who got local electrician John Morley who in turn said the electrics were unsatisfactory which advised contacting STROMA, but it was Matthew Williams, a Council electrician, who carried out an inspection of the electrics at the property for Pembrokeshire County Council Trading Standards. But the report fails to say what was found, and why a report for the vendor was taken up by Pembrokeshire County Council Trading Standards. I could see the conveyancing solicitors raising a court case, but not Pembrokeshire County Council Trading Standards?
This house I had an EIC which was passed off as being for whole house, but was for the flat under the house, and I see no reason why I should be able to claim from the electricians working on the flat for errors in the main house, had it been an EICR for flat same would have applied.