radiator not heating up after one day

Joined
16 Jun 2005
Messages
10
Reaction score
0
Location
Leicestershire
Country
United Kingdom
got a combination cylinder ie cold water cylinder on top feeding hot water and central heating removed a radiator off one wall and extended pipework to fit towel rail on another wall removed all air out system bled all radiators every thing fine day later no heat to new towel radiator think there is a blockage in pipe could one of you nice gents and ladies give me some of your knowledge on what to do please steve
 
Sponsored Links
if that does not help...u can (hopefully) remove the airblock by draining down from the new rad (u did fit a drain valve ?) for about 10 secs or thereabouts...u should hear the air move along...
open the drain valve fast...helps jolt the air lock.
as u say u have f &e system it will top up itself...
 
Sponsored Links
A simple test is to first isolate the towel rail by turning off both its valves.

Remove one of the blanking plugs at the top and replace it with a hose connecter adapter and connect a hose to it and put other end of hose in the toilet.

Opening either valve should give a flow of water out of the hose to confirm there is no blockage.

If there is flow from each valve then after refitting blanking plug it should work but keep your fingers crossed! If not then you may have done something very stupid with the pipe connections like putting both onto the flow side.