RCBO keeps tripping without reason

Thanks AdrianUK.
However it doesn't explain why it trips with nothing connected.
 
Sponsored Links
A neutral-earth fault could do that... the current which flows through the fault need not have come from the circuit in question. I know that seems a strange answer at first, but it becomes apparent why if you draw out the fault path
 
Sponsored Links
OK some observations and test results.
Observations -
during the evening last night the RCBO kept tripping with nothing plugged in (or DP off)
but during the night, I put the boiler on and wife put the dishwasher on - but the RCBO stayed on all night!!!

Tests
1 - the ring is complete (both L & N) - zero ohms.
2 - neither L nor N connect to any other circuit on the CU
3 - L-E, and N-E, and L-N all measure 38M for the ring.
4 - connected L&N across all the CU and the measure 34M between LN-E.

The max age of the wiring in the house is about 28 years
 
Your insulation test results...... taken with a proper insulation tester @ 500V or with a multimeter on 'ohms' range?
 
Tracing obscure reasons for RCD and RCBO tripping requires careful examination of insulation resistance between ALL conductors and ground / earth. This requires disconnection of both Live and Neutral at the consumer unit before insulation resistance tests are carried out.


The fault shown is a dead short. In reality a resistive fault will also cause a trip as will capacitive faults.

Almost all insulation resistance testing is performed with a DC test voltage. This will find resistive leakage paths but will not find leakage paths involving capacitive effects which the RCD will find and react to by tripping.
 
1 - the ring is complete (both L & N) - zero ohms.
:?: Not possible.
True, but we know what he means. Presumably he doesn't have a means of measuring very low resistances. In fact, he seems to have undertaken a true 'continuity test' :)
2 - neither L nor N connect to any other circuit on the CU
:?: How do they work?
I imagine he means 'after the L & N of the circuit in question have been disconnected from the CU - i.e. there are no cross-connections with any other circuit.
3 - L-E, and N-E, and L-N all measure 38M for the ring.
:?:
Does seem a bit surprising. I wonder what is the highest resistance his IR tester can display?
4 - connected L&N across all the CU and the measure 34M between LN-E.
:?:
Again odd, particularly given his results in (3) above. Again, I wonder what is the highest resistance his IR tester can display.

Kind Regards, John
 
True, but we know what he means. Presumably he doesn't have a means of measuring very low resistances. In fact, he seems to have undertaken a true 'continuity test' :)
As he has an IR tester I assumed it would take low ohms measurement.

2 - neither L nor N connect to any other circuit on the CU
:?: How do they work?
I imagine he means 'after the L & N of the circuit in question have been disconnected from the CU - i.e. there are no cross-connections with any other circuit.
Possibly or even probably but, pedantically, not what was said and how can he be certain.

3 - L-E, and N-E, and L-N all measure 38M for the ring.
:?:
Does seem a bit surprising. I wonder what is the highest resistance his IR tester can display?
It won't be 38.

4 - connected L&N across all the CU and the measure 34M between LN-E.
:?:
Again odd, particularly given his results in (3) above. Again, I wonder what is the highest resistance his IR tester can display.
More than 34. :D
 
As he has an IR tester I assumed it would take low ohms measurement.
I didn't think that (m)any 'standalone' IR tests had such a facility?
Possibly or even probably but, pedantically, not what was said and how can he be certain.
True - but do you mean "how can we be certain" ?
Does seem a bit surprising. I wonder what is the highest resistance his IR tester can display?
It won't be 38.
One wouldn't think so, but identical answers for L-N, L-E and N-E would seem very improbable!
Again odd, particularly given his results in (3) above. Again, I wonder what is the highest resistance his IR tester can display.
More than 34. :D
Well, we know it's at least 38MΩ! My point was that if the true IR of three results for individual pairs of conductors which were displayed as 38M were actually >38MΩ, then 34MΩ for L+N/E would be a little more credible.

Whatever, I think we are agreed that the figures are rather odd!

Kind Regards, John
 
As he has an IR tester I assumed it would take low ohms measurement.
I didn't think that (m)any 'standalone' IR tests had such a facility?
Oh. I thought they all did. I may be wrong.


Possibly or even probably but, pedantically, not what was said and how can he be certain.
True - but do you mean "how can we be certain" ?
No. I meant, whilst looking for a fault, how can he be certain.
 
Thanks John for making mostly correct assumptions

1) - yes - continuity round the ring.
2) - yes - L&N disconnected from CU - then checked for cross-connections
3) - see below
4) - see below.

My meter has ranges from 20m >> zero ohms (multi-meter)
My insulation tester goes up to 2000M

After the first set of tests, I discovered the burglar alarm was still plugged in !!
So re-tested and checked insulation for each circuit individually disconnecting from CU as tested.
Fuse--------Circuit--------------- LN------------NE------------LE
1 -----------Shower ----------- >2000 ------- >2000 ------ >2000
2 -----------1st Fl Light ------- >2000 -------- 134 --------->2000
3------------Gnd Light -------- >2000 -------- 149 --------->2000
4 -----------Base Light -------- >2000 ------- >2000 ------>2000
5 -----------1st Fl Ring --------- 1600 --------- 780 ----------1200
6 -----------Gnd Ring ------------ 390 ---------- 34 ----------- 420
7 -----------Base Ring ---------- 1170 ---------1100 -------- 1000
8 -----------Cooker ----------- >2000 ------- >2000 ------>2000

9 -----------Freezer ----------- >2000 ------- >2000 ------>2000
10 ----------Frid/Freezer ------ >2000 ------- >2000 ------>2000
......All in M ohms

yes - I have swapped the RCBOs for gnd and 1st Floor - always gnd floor which trips.
The results above indicate the Gnd floor 'NE' is suspect - but cannot see anything. By the way all wiring is exposed in basement so didn't have to lift floor boards to visually inspect.
 