Had a PIR done yesterday on an installation that it fed from a 7.5KVa generator. This feeds a CU through about 15 mtr of SWA.
All the "dead" tests on the circuits after the CU were ok.
But when the Hager 100A/30mA RCD was tested, it took 60msec at 30mA to disconnect.
The question is this. Is the "high" supply impedance (rel. to a DNO supply) likley to effect the disconnection time?. (Electrician was using a modern "Megger" meter).