My consumer unit has three circuits (up & down sockets & garage) protected by an RCD and all other circuits (including appliance sockets circuit & and a cooker circuit) on the unprotected side. Each circuit has an MCB.
Everything has functioned perfectly since installation (2003) and has the old red/black colours.

I started to install a wall light, using a socket on the upstairs ring, and spurring from it into a switch and onto the lamp.
I left the cable end for the light just cut and protruding from the wall, whilst waiting for the lamp.
However, I found that the RCD kept tripping (but sometimes would hold OK) and sometimes tripped even when the up circuit was off at the MCB. Having checked all connections, I could find no problem, but the trip persisted. Eventually I removed the outer cover from the cable end and seperated the wires. As this has cured the tripping, I can only think that the two cables were insufficiently far apart and that a short was occurring, thus affecting the RCD.
Could this be likely?

Now for a further dilemma. Whilst trying to locate that problem, I had all three circuits switched off at their MCB and the RCD would hold. With any one on at its MCB, the RCD tripped even when the up circuit that I was working on, was off at its MCB. I did not expect that as I cannot see how if there is no flow in the faulty circuit, there could be an inbalance in the circuits across the RCD.
Can someone more knowledgeable explain, please?

And a further can of worms. Again whilst checking, I found that with all 3 circuits off, the RCD would hold on, BUT if the oven on the cooker circuit was switched on, the RCD tripped. Similarly with the washing machine on the appliance circuit. (Their MCB remained on, OK)
As neither of these circuits are on the RCD protected part of the CU, I was surprised and do not understand why? Any explanation would be welcome.
(Seperating that light cable also cured this latter problem.)
 
Sponsored Links
Even though the MCB for a ciruit is swtiched OFF a fault on that circuit between Neutral and Earth is likely to trip the RCD when there is a load taking current on another circuit. Some of the current from that load can bypass the RCD by going through the fault to Earth. Hence the Live and Neutral currents through the RCD are not equal and thus it trips.


Click on image to enlarge
 
I can only think that the two cables were insufficiently far apart and that a short was occurring, thus affecting the RCD.
Could this be likely?
Yes - probably getting wet which could connect the wires.

Now for a further dilemma. Whilst trying to locate that problem, I had all three circuits switched off at their MCB and the RCD would hold. With any one on at its MCB, the RCD tripped even when the up circuit that I was working on, was off at its MCB. I did not expect that as I cannot see how if there is no flow in the faulty circuit, there could be an inbalance in the circuits across the RCD.
Can someone more knowledgeable explain, please?
It's because the MCB only disconnects the Line conductor. Neutral and Earth are still the same.
There will be current in the neutral as a parallel path.
If you touch neutral and earth together, some of this current will flow in the earth and so not return via the RCD.

Depending on the connection between neutral and earth - high or low resistance - only a heavy load will be enough to cause enough current flow to trip the RCD.

Bernard's diagram:

full
 
Many thanks both.
No wonder I went off at a tangent whilst trying to fault find logically!
That cut cable end was not an obvious first port of call.
 
Sponsored Links
Well to bring thread back on topic,

Thanks all, I have added a 5amp FSU, connected from the socket with 2.5mm and on to the switch & light in 1.5mm.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Back
Top