Hi,

I am planning to recharge the expansion vessel on my central heating and need some information. I have heard people say that it has to be removed to recharge it. Is it right? Some others say that I have to drain the Central heating before I pressurise it if I don't remove it. I am confused now. What's the right way? I don't like to remove it completely.
 
Sponsored Links
Joined
8 Apr 2018
Messages
186
Reaction score
45
Country
United Kingdom
De-pressurise you boiler and leave drain cock open while you charge up your expansion vessel to that stated on data plate, normaly around 0.9 bar, close off drain cock, re-pressurise & vent system.
 
Joined
20 Mar 2009
Messages
8,741
Reaction score
1,627
Location
Potters Bar
Country
United Kingdom
Hi,

I am planning to recharge the expansion vessel on my central heating and need some information. I have heard people say that it has to be removed to recharge it. Is it right? Some others say that I have to drain the Central heating before I pressurise it if I don't remove it. I am confused now. What's the right way? I don't like to remove it completely.

Why are you doing this? What problem(s) are you having that leads you to believe this is a remedy?
 
Joined
10 Nov 2009
Messages
17
Reaction score
0
Location
London
Country
United Kingdom
De-pressurise you boiler and leave drain cock open while you charge up your expansion vessel to that stated on data plate, normaly around 0.9 bar, close off drain cock, re-pressurise & vent system.

Thanks, I will follow your instructions.
 
Sponsored Links
Joined
10 Nov 2009
Messages
17
Reaction score
0
Location
London
Country
United Kingdom
Why are you doing this? What problem(s) are you having that leads you to believe this is a remedy?

Checked it using my car tyre pressure reader, shows 0.8 bar whereas the vessel states 1.5 bar as factory fill pressure.
 
Joined
26 Aug 2016
Messages
6,579
Reaction score
926
Country
United Kingdom
Should be slightly below the cold fill pressure of your system. 1.5 may be the factory fill but it's unlikely to be suitable for a normal system. If you over pressurised it relative to the system pressure then even the smallest leak will lose too much pressure very quickly and shut down the boiler.
 
Joined
10 Nov 2009
Messages
17
Reaction score
0
Location
London
Country
United Kingdom
Should be slightly below the cold fill pressure of your system. 1.5 may be the factory fill but it's unlikely to be suitable for a normal system. If you over pressurised it relative to the system pressure then even the smallest leak will lose too much pressure very quickly and shut down the boiler.

Thanks, now I understand. The system pressure currently stands slightly above 1 bar so I think 0.8 bar pressure in the expansion vessel is the right amount .
 
Joined
8 Apr 2018
Messages
186
Reaction score
45
Country
United Kingdom
Thanks, now I understand. The system pressure currently stands slightly above 1 bar so I think 0.8 bar pressure in the expansion vessel is the right amount .
Did you get 0.8 bar when the system was full (pressurised)? You should have around 0.9 when your system is de-pressurised, it makes a big difference.
 
Joined
20 Mar 2009
Messages
8,741
Reaction score
1,627
Location
Potters Bar
Country
United Kingdom
Normally charge them to 1 bar with water side depressurised on the basis you’ll lose 0.1 bar as you undo the pump connector ;)
 