I need some help with my nest install. With my old system I could either have the hot water, or heating and the hot water on. I'd like to be able to select either or/both via the nest.

The old set up: I had an old randall 102 and Honeywell T6360 stat in my 1980s house. It looks like it's an Y plan system, one pump with a T valve, hot water tank in the airing cupboard with two tanks in the loft, a small one (expansion) and a large one. The boiler is a Glow-worm Flexicom 24HX.

New set up: I took out the Honeywell stat and connected the wires together (as per instructions). I run the nest 3rd gen from a dock in the corner of the living room. I replaced the randall 102 with the link unit.

Problem: When I turn the heating on, the nest and nest app says it's heating but the boiler and pump dont kick in. If I turn the hot water on as well then the pump and boiler turn on and the house gets warm, as does the hot water obviously.

Attached are photos of:
-The old and new wire boxes,
-The old randall plate (1 Water on, 2 Heating on, 3 Com, 4 earth, 5 N, 6 L)
-Nest link. L is looped to pins 2 and 5
-The nest link wiring, fyi the red cable from nest 6 that's on the right comes down and around in the bottom of block 11. The red cable from nest L goes to the top of block 10.
-Other info
--The thick white cable on the left goes to the tank thermostat,
--The black cable (look on old wiring box for better light) goes to the valve,
--The dark grey on the right goes down to the boiler, you can see it come back up to a brown round junction box which goes off to the pump
--At the top of the junction box is a thick grey cable, this is the power from the switched spur to the left of the link
-Airing cupboard

I suspect I need to change the wiring, any help would be much appreciated.

Thanks
A
 

Attachments

  • airing cupboard.jpeg
    airing cupboard.jpeg
    290.5 KB · Views: 96
  • New wiring box.jpeg
    New wiring box.jpeg
    299.2 KB · Views: 99
  • Old wiring box.jpeg
    Old wiring box.jpeg
    340.1 KB · Views: 57
  • Overview.jpeg
    Overview.jpeg
    333.2 KB · Views: 97
  • randal 102 plate.jpeg
    randal 102 plate.jpeg
    260.9 KB · Views: 50
  • nest link wiring.jpeg
    nest link wiring.jpeg
    263.1 KB · Views: 51
Last edited:
You need a wire to connect number 4 on the nest to number 9 in your wiring centre.
But you shouldn't be using single insulated wires like you have. You should use a short piece of 3 core flex for the live and neutral and a piece of 4 core for the switch wires.
 
Thank you.

Just to confirm, #9 is linked to #8 which is the grey wire that comes from the thick black cable that runs to the valve.

That was the how it was previously set up. I moved a couple of wires around to make the cables reach the nest link terminal locations, but I can certainly replace those.
 
That is correct. It is the hot water off terminal which connects to the grey wire on the 3 port valve terminal 8 and the satisfied on the cylinder stat terminal 7.
 