Aha! So that's the RCD A80HD! Quite an old one, bigger than the current range, I now understand why it needs an adaptor. If MEM have such an adaptor to make the current size of RCD or Isolator fit, it will be very useful as I doubt you could get the old part any more.
The cable from the meter cabinet to the changover looks rather poor. The cores look undersized and appear to have been wrapped in tape

Possibly this has been done for colour identification, but there is no proper sheathing on them over the insulation. I can't make out what kind of cable it is, is it Steel Wire Armoured? If so, it has not been properly terminated.
However as there is an 80A switchfuse between the metar tails and that other cable, it could safely be isolated to replace the cable with something larger. What is the distance between the meter cabinet and your changeover switch?
I see you have another rusty switchfuse and an old fusebox next to the changeover switch, what do these do?
The MCB for the cooker is a GE one, not MEM, so should be replaced as it may not be a good fit.
The second MCB from the left is a MEM one, later model than the others, as currently issued. Are its dimensions and fit the same as the old one?