ring main connected with connector block

Joined
25 Dec 2007
Messages
153
Reaction score
1
Country
United Kingdom
Hi all,

our elec has made a fuss over a ring main connected with one of the white connectors. Is this against the regs? I think the previous owner did this because the main was too short to reach the CU.

Regards,
 
that depends, using terminal block is not in itself a problem. Using terminal block that is too small is a problem. Using terminal block without a suitable enclosure is a problem. Using terminal block where is can't be accessed for inspection is a problem.
 
there is usually no need, you can put in an extra socket instead. it might be useful.
 