Hi,
I am looking into installing a ring main in plastic PVC conduit around a room. The room is approx 75m² floor surface area. I will be looking to install 4 double sockets. The wire will be 2.5mm² for both live conductors and CPC. The conductor lengths will be approx 50m end to end.
The earth fault loop impedance (measured) at the consumer unit in the room is 0.3ohms. Am I OK to install the above protected by a 32A type C RCBO? Square D do not appear to manufacture a type B in the KQ range.
Paul F.