Ring main

Joined
8 May 2009
Messages
35
Reaction score
0
Location
Sheffield
Country
United Kingdom
ok had an extension done

put 10 new sockets in a ring. but only one feed coming from consumer box. is this ok or do i need to get a return to the consumer box?

just to clarify, i have one main coming from consumer unit and going to the back of a socket and then a feed from the socket to the other sockets until the last, 10th socket with a single feed from the previous socket. is this ok? Do i need a feed from the 10th socket back to the consumer board?

It all works ok.

Please help.
 
Sponsored Links
If you have a 16a mcb fitted fine. If 32a you need to add the "return leg" to make a ring. And RCD protection and testing…and….. :eek: signed off by an electrician.

DS
 
From his description it's a radial, and isn't necessarily either forbidden or dangerous - depends on the size of the cable and the rating of the protective device.

Krazaq - was the electrical work done by someone who self-certified Building Regulations compliance, or was it notified in advance to Building Control?

What does the schedule on your Electrical Installation Certificate say about cable size, MCB rating, circuit type etc?
 
Sponsored Links
6a ? 10 a ? …….. your point is ?

As the installation method is not given i would not suggest 20a or 25a.


Kind regards,

DS ……….. COULD BE BELL WIRE :p
 
the cable is the normal socket cable running from consumer unit with fuse b32.

Yes its just a long spur.....
 
Can i just simply put a another single mcb consumer unit using the main feed from the consumer box and then wire the circuit to it, i.e sockets 1 to 10.
 
6a ? 10 a ? …….. your point is ? ... As the installation method is not given i would not suggest 20a or 25a.
... nor was the CSA given, so even to suggest that a 16A MCB would be 'fine' involves an assumption. I presume that EFLI's point was that you seemed to imply that there were no possible (not certain, without additional information) alternatives to a 16A MCB other than to convert it into a 32A ring (again with assumptions about the CSA and installation method!).

Kind Regards, John
 
Can i just simply put a another single mcb consumer unit using the main feed from the consumer box and then wire the circuit to it, i.e sockets 1 to 10.
I don't fully understand, but the answer is almost certainly 'no'. You really need an electrician, and what (s)he would probably do is run a cable from the last socket back to the same B32 MCB in your CU to which the first socket is connected.

Kind Regards, John
typo corrected
 
If you have a 16a mcb fitted fine. If 32a you need to add the "return leg" to make a ring. And RCD protection and testing…and….. :eek: signed off by an electrician.

DS

I think i said that.

DS
 