Running 4 core armoured cable to power shed

Discussion in 'Electrics UK' started by mikex, 25 Nov 2008.

  1. mikex

    mikex

    Joined:
    25 Nov 2008
    Messages:
    2
    Thanks Received:
    0
    Location:
    Devon
    Country:
    United Kingdom
    I am connecting a 4 core armoured cable to a fused outside connection terminal and to a mini RCD consumer unit in the shed to run 2 sockets and a light. The cable has 4 2.5mm wires (Black, Brown, Blue and Grey)plus armoured wire sheathing. I have been told that I just connect 3 wires and ignore the 4th & sheathing. However I read somewhere that I should earth the sheathing..Can somebody please advise the correct wiring method. :rolleyes:
     
  2. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,787
    Thanks Received:
    2,857
    Location:
    London
    Country:
    United Kingdom
    You must earth the armour.

    You must use proper external SWA glands.

    You must install the cable safely.

    You must ensure that the cable is the right size to avoid excessive volt-drop.

    If you've got a CU at the shed end you must ensure that you don't get discrimination issues with one in the house.

    Are you aware that this is notifiable work? See here: http://www.diynot.com/wiki/electrics:part-p
     