To quote you
A horizontal wire will lose convective heat away from the wire. A vertical wire will lose heat into the same space as the wire above it, heating it up.
As I see it the basic physics is that there are 3 ways in which heat can be dissapated away.
1. Convection currents through gas or liquid, this is the heat rises case.
2. Conduction - through solids - in all directions equally.
3. Radiation - through everything (almost) - in all directions equally
So considering our wire.
Convection currents will be set up only after the heat has been dissipated to free air, in our case through the insulation it is surrounded by, so it matters not whether it is vertical or horizontal. Conduction conducts equally in all directions, as does radiation. So I don't believe there is a case for considering the orientation of the wire when deciding whether to use Method 103.
Even if we look Table 52.2 it would have us derate the cable by 0.51 if it were run in any longer length than 400mm which is 13.77A for 2.5mm t/e.
So we are back to 4mm.
Sorry if this appears to teach granny how to suck eggs.
Martin
A horizontal wire will lose convective heat away from the wire. A vertical wire will lose heat into the same space as the wire above it, heating it up.
As I see it the basic physics is that there are 3 ways in which heat can be dissapated away.
1. Convection currents through gas or liquid, this is the heat rises case.
2. Conduction - through solids - in all directions equally.
3. Radiation - through everything (almost) - in all directions equally
So considering our wire.
Convection currents will be set up only after the heat has been dissipated to free air, in our case through the insulation it is surrounded by, so it matters not whether it is vertical or horizontal. Conduction conducts equally in all directions, as does radiation. So I don't believe there is a case for considering the orientation of the wire when deciding whether to use Method 103.
Even if we look Table 52.2 it would have us derate the cable by 0.51 if it were run in any longer length than 400mm which is 13.77A for 2.5mm t/e.
So we are back to 4mm.
Sorry if this appears to teach granny how to suck eggs.
Martin