Running water noise from boiler

Discussion in 'Plumbing and Central Heating' started by NotebookNewport, 7 Apr 2021.

  1. NotebookNewport

    NotebookNewport

    Joined:
    11 Jul 2015
    Messages:
    186
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi
    Worcester Greenstar 30i Combi ErP
    Just had some plumbing done with a new shower and bathroom. the condenser pipe was rerouted and since I can hear the sound of trickling water inside the boiler when the heating is on.
    temporarily I had it running into a bucket while work carried out. No noise apart when it discharged.
    The pipe shown runs to a soil pipe.
    Any ideas?
    No loss of water anywhere
     

    Attached Files:

    Last edited: 11 Apr 2021
  2. Sponsored Links
  3. NotebookNewport

    NotebookNewport

    Joined:
    11 Jul 2015
    Messages:
    186
    Thanks Received:
    0
    Country:
    United Kingdom
  4. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    12,854
    Thanks Received:
    2,872
    Location:
    Daventry
    Country:
    United Kingdom
    And the boiler is?
     
  5. NotebookNewport

    NotebookNewport

    Joined:
    11 Jul 2015
    Messages:
    186
    Thanks Received:
    0
    Country:
    United Kingdom
    Sorry
    Worcester Greenstar 30i Combi ErP
     
  6. Sponsored Links
  7. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,284
    Thanks Received:
    472
    Location:
    London
    Country:
    United Kingdom
    I'm pretty sure that boiler has an internal trap for the condensate. You show it flowing into a trapped drain, so two traps. This means that air can't get back into the boiler's trap. Try removing the rubber "bung" at the top of the pictured trap and see if that makes a difference. If it does, then provided the drain pipe runs straight into a drain with an air gap, remove the trap in yor picture and connect directly.
     
    • Thanks Thanks x 1
  8. NotebookNewport

    NotebookNewport

    Joined:
    11 Jul 2015
    Messages:
    186
    Thanks Received:
    0
    Country:
    United Kingdom
    will do - where would I find out about the internal trap?
    the pipe is running into the soil pipe
    before that, I had it running temporarily without trap etc and into a bucket - worked fine, so you might be onto something
    Thanks
     
  9. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,284
    Thanks Received:
    472
    Location:
    London
    Country:
    United Kingdom
    Check the installation instructions for your boiler. Available on-line if you don't have a hard copy.
     
    • Thanks Thanks x 1
  10. NotebookNewport

    NotebookNewport

    Joined:
    11 Jul 2015
    Messages:
    186
    Thanks Received:
    0
    Country:
    United Kingdom
    Ok. Loosened the seal as you said et voila. Water running out of the boiler down the pipe. Noise gone.
    You beauty.
    Thanks so much
     