Mate of mine lives in a beautiful historic 3 storey house. Over the last couple of years I have done a fair bit of work there. Installed a kitchen, and recently 2 bathrooms.

On the 3rd floor there are 2 large bedrooms unoccupied and a bathroom. The bath had mixer taps and he asked me if I would fit one of those power shower units to give a bit more oomph to the gravity fed water system. I explained that RCD protection would be required as the house is supplied by 2 x Wylex CU's with BS3036 type fuses.

No problem was his reply let's replace both boards with 2 new boards with RCD's and mcb's. Have to admit because of the tail/cable positions it was a much easier job to put in the 2 new CU's without having to extend any cables.

Because of the nature of RCD's I extensively tested the circuits before proceeding with the replacement of the CU's. On IR tests all circuits were showing >199MOhms except 1 circuit that was reading 4.21 Mohms. Now I know it is within the limit but it seemed curious to me so I suggested this circuit be retested 6 months down the line to see if any further degradation had occurred.

So I proceeded to install the 2 new boards, filled in the certs and said I would return next week to install the power shower.

I returned next week and commenced the power shower. A heavenly job as I was allocated an empty bedroom to store tools and materials because its a long way up them stairs. Plugged the radio in and started work. Put an FCU outside the bathroom (luckily the ring ran right across the landing. Ripped down the lathe and plaster wall at the head of the bath , put in the plumbing and electrical feed. Boarded up.

Whilst I'm working the radio cuts out. Test the lights, they've gone to. Run downstairs to find the RCD tripped. Do an IR on the new cable..it's fine. Turn the RCD on and do a loop test..all fine. Now I'm stumped.

Any way over the next few days the RCD keeps tripping. Sometimes 10 minutes between trips sometimes a few hours. I point out to my mate we seem to have a problem with the RCD that protects the upper floor power/lights and the stairwell/ outside lights. Luckily for me the first 2 floors are unaffected so my mate is not inconvenienced.

Next day I ask him did it trip during the previous evening..he says no. Go back to work on the upper floor and the same frequency of tripping occurs yet again. I'm beginning to tear out my hair now. My radio is the only appliance plugged so I unplug it. Still the RCD keeps tripping.

Next thing I do is turn off all the circuits bar 1 (hoping its a L to E fault). Now pattern emerges so I'm unable to narrow down the faulty circuit. I'm fast coming to the conclusion its a N/E fault.

This pattern keeps re-occurring...many trips during the day but only the occasional 1 during the evening.

Anyway, finish the shower, test and commission. Ask my mate to keep a log of any RCD trips and keep me updated. No telephone calls for a long time. Then out of the blue comes a weekend of many trips. I go back and on a hunch decide to retest the RCD.

Eureka!!!! the damn thing is tripping on the half test. Take out the defective RCD, quick trip to TLC, get replacement and reinstall. Retest and the RCD is doing what is says on the can. I am relieved.

A few more weeks pass and I get a telephone call...the damn thing is tripping again. The situation is made worsen by the fact they have a house guest on the the 3rd floor. I go round and Ireally don't know what to suggest..I'm clutching at straws. I look inside some power sockets and they are caked with dust so I'm wondering if this could be the problem. Also the sockets are 20 years old so maybe a bit of current is tracking to earth.

My mate says he will replace the sockets. But that lighting circuit is still troubling me. 4.21 Mohms on the IR test. Will it mean lifting up his beautifully polished or painted floorboards? Will it mean chasing out the walls and replaing cables? This is a house that is all uptogether so I'm nervous about suggesting this course of action.

few days later I get a call the problem has been solved by the house guest, and I'm invited round. My mate takes me into the bathroom and calls the young female house guest. He turns on the lights and says to the young girl....'Show him your trick'..............

Any ideas lads? I'll post photos shortly
 
Sponsored Links
Spot on RF...Hehehehe...No surprise you got it!!!. The floorboard was firmly fixed down with caulked joints. The floorboard in question was sited just to the right of the basin.
She was only a slither of a thing so this was an amazingly sensitive trigger. I must have tripped it dozens of times without me realising I'd done it. Well done mate!!!



A beautiful house doesn't always guarantee beautful wiring
 
Sponsored Links
I only got it cos I got called to a similar one a good few years back, only they didn't have any RCDs and the circuit supplied the shower.

Unfortunatley it was before phones had cameras, so I didn't get a photo of it in situe.

Here's what was left of the 6mil cable.

IMGP1012.jpg


:eek:
 
RF that looks horrific. Was it the result of a nail? In my pic the cable had somehow got trapped between the rim of the clout nail and the joist and had split the thermoplastic and then chipped away the neutral insulation. It's amazing when you lift floor boards in the old housing stock here in Pompey.
It seems all rewires take advantage of notched joists and frequently run alongside heating pipes. Not that often that you see the joists properley drilled. The good thing is more people are aware of Part P so now the standard of install is rising.[/b]
 
Yes it was a nail thru a floorboard straight into the cable. I don't know how long it had taken to get into that state. The cable was still live when I got there. The call was that their shower had stopped working.

I think it was more luck than anything which stopped the floorboard and joist catching fire. It's one of the worst things I've ever found.

It was supplied from a ~40A BS3036 fuse which had not operated.
 
I think it was more luck than anything which stopped the floorboard and joist catching fire. It's one of the worst things I've ever found. It was supplied from a ~40A BS3036 fuse which had not operated.
I guess it's like wot I was saying recently about the circuit with a known fault that was left energised 'temporarily'. I think we often derive too much, potentially false, confidence from the presence of OPDs - as I said before, a current well below that which will operate an OPD is quite capable of doing a lot of damage and potentially starting a fire - just think about how little current it takes to get the filament of an incandescent lamp very hot!

Kind Regards, John.
 
:?:

Sorry.

Mod, please delete.

This was in response to a post that has since disappeared.
 
Do you have any ideas/guesses on what's motivating that pillock to register here day after day after day and make those pointless posts? He's not even spamming anything.
 