When doing P.I.R and the service is sealed what do you put on your report ? I called the supplier and he said they dont keep records of what fuse is used etc ,then he said I will check for you and had me on hold for 13 mins on a 0845 number from my mobile so I let it go..
 
Sponsored Links
What sort of premises are we talking?

If its just standard <= 100A head, then make some assumptions and put N/V - (not verified) by the side of it. if its something like a series 5 or series 7 cutout etc, then its going to be a BS1361 IIb, rupering capacity of these is 33ka. as for rating then there might be an adhesive label fitted, "80A FUSE FITTED" is what CN/WPD stick on around here now. If not then state the rating of the carrier (usually 100A, but sometimes 60A) with N/V marked after it
 