It sounds like you have 'TT' installation (see the pics in for reference for what that means, and see if that is true or not)
If so you have an outside earth rod only (and no company earth) and this will have a resistace of 10 ohms to perhaps a few hundred depending on the dampness of recent weather and how corroded it is.
Because a 100 ohms to earth will not blow a fuse or fire an MCB, but just make the rod live, and give you a large electricity bill, it is a requirement ot have something that positively disconnects the supply if a fault to earth occurs.
The old way was to put a trip that measured the current going to the earth rod, but as this does not detect faults where the fault current flows through you into the garden pond or the plumbing, this method has been depracated for many years, in favour of the RCD, which compares live (outbound) and neutral (return) currents, and if not exactly equal and opposite, cuts the juice (as any fault where current goes out the live and doesn't come back down the neutral is a bad thing....).
Such a device has 4 terminals, live and neutral in and out, but no earth connection is needed. Nowadays one of these in a plastic box should be the first thing after the meter on a TT installation.
If it is not just one 30mA trip for the whole lot (which can give nuiscence tripping), then a 100ma slow acting ('time delay') for the whole lot, and then a 30mA type for all socket circuits that might serve outdoors.
So a T.D. in a plastic box of its own, then a split load board is a good possibility.
The old trip should go, and I'd suggest looking at the earth rod, and seeing if a new one might be in order - it should be hammered in somewhere wet, and installed in a proper 'pit'. See the TLC website for pictures. Installing the new RCD in place of the old trip is probably not a DIY job unless very confident, as the main fuses will have to be pulled and the electricity board (DNO) will want to be involved in that.
Nothing to stop you doing as much of the enabling work as possible though.
regards M.