To clarify - if you really don't have a company earth or an external earth rod, then you have a TT supply as it used to be in the days when main water pipes were lead (I presume they have been changed for copper of polyethylene by now?). You should look for somewhere where the earth is pretty much permanently moist to add the earth spike as a first step, and it matters little if you have an RCD as the main incomer in a plastic split load box or a single box, that is then feeding one or more more 'normal' consumer units, (which may then be metal if you like) but in either case the electrical effect is the same.
Most 100mA RCDs are not time delay sadly, and a fair number of suppliers are a bit woolly on this point in their data too.
Personally I think the maker of the trip is not as important as the quality of the box it goes into - you don't want a flexi- CU with not enough mounting holes, where there is no room to put the wires in properly. (Volex are have bad name for that sort of 'over economy', but most sparks have their personal hates / favourites. It doesn't mean its no good at all, or actively dangerous if installed carefully, but it might be the difference between an easy job, and a messy one.)
I presume in practice the trip doesn't fire very often at the moment, so there is not a great risk to the 'one fault trips all' problem, after all the company fuse is a single point of failure, but if it never blows who cares...
however, if you anticipate much tripping and wish to avoid the 100mA delay RCD, you could have more than one plastic box with an RCD incomer in each, say one for lights one for power. It doesn't need to be time delay then, as there is no risk of a 'race', as they are independent.
Probably worth costing up the different options.
regards M.