Hi all,
I'm after some advice and clarification on a few points for a proposed supply to two outbuildings in my garden, a shed/workshop I've just built and a small BBQ cabin further down the garden, neither of these have any water/gas supplies into them and are of timber construction.
Firstly, I'm not an electrician (obviously) however I do hope to do as much of the work myself as I can but I'll be paying for the entire install to be checked by a qualified electrician prior to them connecting everything to mains inside the house. As I live in Scotland the work is not notifiable to my understanding.
My supply is TN-C-S so I gather the outbuildings will need to be earthed locally by the means of an earth rod rather than exporting the earth.
I have no additional capacity in my house consumer unit so will need tails to a new small metal 1 way CU in house for the external supply. The run from the house to the shed/workshop is 15m and I'll use 10mm SWA and the shed/workshop to the BBQ cabin run is 25m of 3-core 10mm SWA (this is already buried during recent garden re-landscape)
The shed/workshop will have the following:
5 way insulated consumer unit with 30ma RCD
1 x 6amp MCB for lighting circuit (12 LED downlights)
1 x 32amp MCB for 4mm2 radial socket circuit (8 double sockets for various power tools, desktop computer, small fridge & occasional use of a small electric heater)
1 x 16amp Type-C MCB for a single 16amp plug (for occasional use of a small MIG welder)
1 x 32amp MCB to supply BBQ cabin
The BBQ cabin will have the following:
2 way insulated consumer unit with or without 30ma RCD??
1 x 6 amp MCB for lighting circuit (for 10 LED downlights)
1 x 16 amp MCB for socket ring (for 4 double sockets for low power devices & occasional use of a small electric heater)
The earthing requirements, can I get some clarification?
As not exporting the earth from the house supply it would be a local earth rod (or rods) behind the shed (nice damp clay ground, never really dries out), copper 5/8inch rods with 6mm2 cable running in conduit into the shed CU earth bar?Can this then be taken via the 3rd core (this cable is already in place) of the SWA from the shed to the BBQ cabin or does the cabin also need to have a local earth rod fitted?
Protecting the armour of the SWA, the armour would be earthed at the source end via gland banjo's to the TN-C-S earth in the house is that correct? The house-shed run of SWA and the shed-cabin run would both enter an adaptable box (using glands obviously) on the exterior of the shed, to protect the armour of the shed-cabin run can the two banjo's be bolted together in the adaptable box to give continuity of the armour, therefore the 25m run from shed-cabin would also be protected have I got that right?
Regards RCD's...
I'll be protecting the shed circuits and cabin with a 30ma RCD in the shed CU, I'm not sure if there is any need for an additional RCD in the cabins small CU and also at the supply end? I've read about time delayed 100ma RCD's at the supply end however, although that seemed to relate to the domestic supply being TT rather than the outbuildings themselves.
I'd really appreciate any advice anyone can offer on these points or indeed any aspect of the proposed installation.
Kind Regards
I'm after some advice and clarification on a few points for a proposed supply to two outbuildings in my garden, a shed/workshop I've just built and a small BBQ cabin further down the garden, neither of these have any water/gas supplies into them and are of timber construction.
Firstly, I'm not an electrician (obviously) however I do hope to do as much of the work myself as I can but I'll be paying for the entire install to be checked by a qualified electrician prior to them connecting everything to mains inside the house. As I live in Scotland the work is not notifiable to my understanding.
My supply is TN-C-S so I gather the outbuildings will need to be earthed locally by the means of an earth rod rather than exporting the earth.
I have no additional capacity in my house consumer unit so will need tails to a new small metal 1 way CU in house for the external supply. The run from the house to the shed/workshop is 15m and I'll use 10mm SWA and the shed/workshop to the BBQ cabin run is 25m of 3-core 10mm SWA (this is already buried during recent garden re-landscape)
The shed/workshop will have the following:
5 way insulated consumer unit with 30ma RCD
1 x 6amp MCB for lighting circuit (12 LED downlights)
1 x 32amp MCB for 4mm2 radial socket circuit (8 double sockets for various power tools, desktop computer, small fridge & occasional use of a small electric heater)
1 x 16amp Type-C MCB for a single 16amp plug (for occasional use of a small MIG welder)
1 x 32amp MCB to supply BBQ cabin
The BBQ cabin will have the following:
2 way insulated consumer unit with or without 30ma RCD??
1 x 6 amp MCB for lighting circuit (for 10 LED downlights)
1 x 16 amp MCB for socket ring (for 4 double sockets for low power devices & occasional use of a small electric heater)
The earthing requirements, can I get some clarification?
As not exporting the earth from the house supply it would be a local earth rod (or rods) behind the shed (nice damp clay ground, never really dries out), copper 5/8inch rods with 6mm2 cable running in conduit into the shed CU earth bar?Can this then be taken via the 3rd core (this cable is already in place) of the SWA from the shed to the BBQ cabin or does the cabin also need to have a local earth rod fitted?
Protecting the armour of the SWA, the armour would be earthed at the source end via gland banjo's to the TN-C-S earth in the house is that correct? The house-shed run of SWA and the shed-cabin run would both enter an adaptable box (using glands obviously) on the exterior of the shed, to protect the armour of the shed-cabin run can the two banjo's be bolted together in the adaptable box to give continuity of the armour, therefore the 25m run from shed-cabin would also be protected have I got that right?
Regards RCD's...
I'll be protecting the shed circuits and cabin with a 30ma RCD in the shed CU, I'm not sure if there is any need for an additional RCD in the cabins small CU and also at the supply end? I've read about time delayed 100ma RCD's at the supply end however, although that seemed to relate to the domestic supply being TT rather than the outbuildings themselves.
I'd really appreciate any advice anyone can offer on these points or indeed any aspect of the proposed installation.