I have also opened up all of the radiator regulator valves.
Why? You have now completely upset the system balance - assuming it had been correctly balanced before.
I am reluctant to deduce the pump speed any more in case I go below the manufacturers minimum flow rate through the boiler of 1200 litres per hr.
The flow rate quoted refers to when the boiler is running at max output. It is calculated based on a maximum temperature differential of 20C. If the same flow rate is maintained when the boiler is producing half the max output, the differential will be half, i.e. 10C. If you want to maintain the same differential then you must reduce the flow rate proportionately.
The minimum output of your boiler is 5.7kW, so the minimum flow rate is 230 litres/hr for a 20C differential.
Referring back to my opening post, how can you tell from the pump curves what the flow rate is?
To calculate that, you need to know how many kW the boiler was producing.
If you have a 12C differential and assume the boiler is running at max output, the flow rate is 2024 litres/hr.
You could also estimate it from the
pump curves
Look at the second graph down (P1/W). Draw a line horizontally from 30W on the vertical axis until you meet the 3m line (not there but you can assume it's halfway between 2m and 4m. This will occur at approx 2 on the horizontal axis. This is 2000 litres/hr.
Whichever way you do it, the flow rate is twice the required minimum.
How did you obtain the output of your radiators?