Shower Cable in wall
Have you a test/multimeter?
If, from your main earth terminal (usually in the CU) to structural metalwork (pipework) has a resistance of greater than 22ohms then 'earthing' is not required.
John, this statement is 10 x worse than the one about the '0.05' ........you're slipping.
And 'Scoby_Beasley', you really need to make sure of your facts before posting advice. :)
Whoops :oops: Indeed! I confess that, in haste, I read that at 22kΩ - which didn't sound too far off the mark.
Very much so - that was crazy 'advice'.
Kind Regards, John
yup that busy finding the ohm symbol, which I didn't I forgot the (capital) K as in 22KΩ
Using an MFT:
I = V / R;
I = 500V / 22000Ω = 0.023Amp
If the fault was on a single phase 230V supply the current that would flow between the conductive parts would be only 0.0115Amp or 11.5 mA. Just above the 'let go' of 10mA.
This is unlikely to give a fatal shock.
It's the other way round.
10mA is used to determine the resistance.
230V / 10mA = 23,000Ω
Never see the point of deducting 1,000Ω for the human body.
It's not going to be 21,999 or 23,001 is it?
More likely to be 240V anyway, so 24,000Ω
True. Sometimes my head hurts. Where's my medication???