One can but presume that it was either installed as 'provision' for something inthe future,or else whatever it was supplying has been removed.It definitely only has two cables, both connected to supply. It just seemed odd that it exists in a modern build home but doesn't appear to have any purpose.
Yes, as I said, you can have one 'socket' supplied as an unfused spur from the supply side. For better or for the worse, the regulations allow just one 'socket' - one single socket or one double socket (but not two single sockets) on an unfused spur.Would it be possible to connect one dual gang twin power socket as a spur from the supply side of the FCU? You mentioned a single socket being possible in your earlier post but did you mean that literally as one single power socket?
If you wanted more than one socket on a spur, it would have to be a fused spur. However, you could replace the current switched FCU with an unswitched one, to address the issue you have mentioned. You could then run as many sockets as you wanted fromthe load side of that FCU, with the total 13A load limit.I'd like the dual gang power sockets to not be controlled by the switch on the fused switched spur.
Kind Regards, John
Thanks for all the detail.
I only really require one more dual gang twin sockets as I think 4 plug sockets behind a TV ought to be enough.
Would another alternative be that the FCU could be changed for one dual gang twin socket?
Regards
Justin