Socket query

Joined
8 Jun 2008
Messages
14
Reaction score
0
Location
Staffordshire
Country
United Kingdom
Im going to install a metal double socket onto my garage wall. Because its metal do i also need to earth the back mounting plate on the socket.

If so, does the earth cable have to be of a certain type. i've some spare arctic flex cable i used for an outdoor light and have stripped it down to get the earth cable out, is that ok to use for earthing the back plate?

many Thanks
James
 
Sponsored Links
As long as the csa of the earth is 1.5 mm or above, then OK. You could also just strip the earth out of the 2.5 twin and earth you're using to put in the new socket..
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top