Soil stack vent for 2 connections to foul drains

Discussion in 'Plumbing and Central Heating' started by Tarik, 13 Dec 2019.

  1. Tarik

    Tarik

    Joined:
    13 Dec 2019
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    My house has 2 connections into the main foul drainage within 1m of each other and the idea is that 5 toilets will connect to both of these following an extension. I fell out with the builder that did it like this so I'm not sure what the exact plan was. I know that usually you would have one soil stack that sticks out of the roof or you have an air admittance valve but when you have 2 connections do you need 2 soil stacks or do you connect these 2 stacks together within the property and have 1 soil stack? One connection will be used for 2 ground floor toilets and the other will have 2 first floor and one loft toilet going into it.
     
  2. Hugh Jaleak

    Hugh Jaleak

    Joined:
    3 Feb 2008
    Messages:
    6,483
    Thanks Received:
    1,446
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Ground floor WC's can be directly connected to the drain, but given you have 2, I'd use a stub stack, and cap that with an AAV. Upper floors into a Vented stack. No need to join the 2 stacks.
     
  3. Sponsored Links
  4. Tarik

    Tarik

    Joined:
    13 Dec 2019
    Messages:
    8
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks for your suggestion Hugh. In that scenario, would the pipe that has toilets on it on the upper levels have a soil stack that goes through the roof or a high AAV and the other pipe with toilets on the ground floor have it's own AAV which would be a bit above the ground floor toilet height?
     
  5. Hugh Jaleak

    Hugh Jaleak

    Joined:
    3 Feb 2008
    Messages:
    6,483
    Thanks Received:
    1,446
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Yes, one stack ideally needs to be vented to allow any positive pressure in the system to escape, if you cap them both with an AAV then you may find you have issues going forward and will end up fitting a vent anyway.

    Upstairs WC's put into vented stack, ground floor into stub stack, AAV needs to be above spillover level of the highest appliance, so if you're having a basin in the WC, bear that in mind when doing your calcs.
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page