I’ll monitor it closely tomorrow but I’m sure the pump constantly runs, the display only shows one temp which I believe is the AUX sensor (on instructions) which I think is the top of the hot water tank , I cannot see the collector temp other than manually read with multimeter, I’ve had it on just over 2hrs and it’s gained about 20° (started on about 15° it’s at 35° ish )
Cheers I’ll try that tomorrow to
Not sure what the 10 tube area is but probably around 1.7M2.
If you heated a full cylinder of water from 15C to 35C (unlikely?) then the tubes output was 140*10/860, 1.63kW, pretty good, and even if it only heated say 1/2 the cylinder, then output still 0.82kW.
You posted at 1413 hrs that the cylinder temp was 35C, did it subsequently rise further or was HW beig drawn off?.
You would want to keep a good eye on the tubes temperature while the pump is off, especially if very sunny, you don't want to thermally shock the system if the tubes get very hot which they (should) definitely will if pump left off for a hour, at 1.5bar pressure the saturation temperature (boiling point) of "water" is 128C so best keep well below that, suggest a max temp of 75C/80C and then re enable the pump.